2 x Sunsynk 50 kw hv inverters with 2 x freedom won 60/48 volts high voltage battery
Good day
Has any one figured out the communication protocol between the 50 kw hv inverter and the freedom won hv battery
Can someone share the cable configuration for inverter and battery communication.
And also one of the batteries trips even without load on the slave inverter.
You can respond to my emai at chirozvacn12@gmail.com or whatsapp number +26710988045
My client bought the equipment on the installer. I have never experienced this problem
And I desperately need a solution
Regards
Chris
55 Views

Following on from my previous comment it does look like they do support Sunsynk (as shown in this table).
You still need to make sure the controller is programmed for this inverter.
WRT to the comms cable it looks like a standard Cat5/Cat6 cable can be used between the battery and the inverter.