Battery BMS and restart voltage

My SunSynk 5kw inverter cannot communicate with the BMS on the 2 Pylontech batteries. In this video (https://www.youtube.com/watch?v=UQPtwkWgpEQ), it is suggested that the Shut Down, Low Battery and Restart voltages need to be set manually for the BMS to work correctly. I checked the Pylontech manual and it does not include these voltages. Does anyone have the correct voltages?


ree

111 Views
Flipper
Flipper
Jun 25, 2023

Pylontech recommend 50A limit per batterie. You have two US 5000 so therefor you can go up to 100A. I limit my charge current to 60A for my three Pylontech batteries. 20A per battery. My discharge current is 100A between the three so well within spec. In that way I protect them with lower amps. My max charge watts from my pv is 3100 watts.