Sizing PV Surge Protector

I have a 5.5kw Inverter with 6 x JA Solar 545 Panels in series with

Open Circuit Voltage(Voc) [V] = 49.75, Total Open Circuit Voltage(Voc) [V] = 298.5

Maximum Power Voltage(Vmp)[V] = 41.80, Total Maximum Power Voltage(Vmp)[V] = 250


I have installed a 275V Surge Protector, by sizing for Voc and max inverter voltage. Should I have sized for Vmp instead? What voltage surge protector is suitable?

Assumed that it should would never go above the the Maximum Power Voltage, but it does around midday and I think it is being cut by the Surge Protector.



ree





57 Views
Groots
Aug 01, 2023

To protect PV is normal to protect against lightening strikes or indirect lightening strikes. SPD's are normally using a voltage range between 1000V and 1500V well above the total Voc of you panels and provide a voltage protection level of somewhere between 3kV and 5kV, so a 275V SPD is way to small for the solar PV. A 275V SPD isnormally the size you would use on the 240V AC side.