Solar Potential vs MPTT
I have a SUNSYNK-8K-SG01LP1 unit.The max. PV Input Power is 11.4kW listed on the side of the inverter. 1. If my solar potential is 13kW, will the inverter "clip / limit" to 11.4kW, or will the inverter be damaged? 2. Will the PV Input current be limmited to 22Adc per MPTT and not draw more than 22Adc?
My plan is as follow:
East Facing: 2x string of 6x Canadian Solar(454W) panels (49.6Voc)
West Facing: 2x string of 6x Canadian Solar(454W) panels (49.6Voc)
2x East Facing strings on MPPT1 (+-297.6Vdc) @ 21.975Adc - 12 panels
2x West Facing strings on MPPT2 (+-297.6Vdc) @ 21.975Adc - 12 panels
Is this correct or am i missing something?
81 Views

It should work fine. I was just curious why he had decided to do it that way.