I need help to set the settings in the eastron mct.
I have 80 ampere on 50 kw inverter and the house totalload is 160 ampere and 400 volt.
I cant adjust the setting ct2 from 1 A to 5 A ..... then it says Err.
Is there an factory reset ?
Hope someone will help
71 Views







Thanks, it work.
What about all the other settings, is they nessesery and have anyone maybe a list of presettings so the settings is correctly in synk with the 50 kw inverter.
( i have ajusted the CT coil settings so they are correctly match with they coils i have used. )