16kw inverter in three phase setup
Hi. Having a weird problem. Setup is 3x 16kw Sunsynk inverters with a Freedom one battery. When grid is present, output is 380 between phases. The problem is when running "off-grid" with no grid supply, the voltage between the phases is 200V. Each inverter measures 228v between its L and N. Setup is all dipswitches up position, parallel selected. Inverter 1 is phase A with modbus 1, inverter 2 is phase B with modbus 2 and inverter 3 is pahse c with modbus 3. All three gose to "normal" mode (LED) at the same time and there is comms between the inverters and also to the battery.
Please help.
Sorted. It seems it was the neutral/earth bond.