If i have a 5kw sunsynk inverter with ct installed, plugs and lights connected to load port.can i set the power limit to 6kw and that

Then means that, when grid is available , that i can draw 6kw in total for essentials and non essentials at the same time? Or what does th

Inverter power limit setting do?

97 Ansichten
Flipper
Flipper
Aug 03, 2023

Rookie. No it will not solve your problem and will trip every time. 5kw is the most you can export to your non essential or grid. Your non essential loads does not go through your inverter and is isolated and off during load-shedding. When the grid is available excess pv will supply the non-critical side. You can set the limit to what you want to export to the grid but it will have to be within the 5 kw of your inverter size which your's is. My suggestion would be to have the washing machine and dryer on the non essential side.

You can draw as much power from the grid as your main DB braker can handle but your inverter can only handle the 5.5 kw it is rated for.

You also have only one 5kw battery which in itself can only supply 5kw of power(C-rating permitting).

You can set the intervals on the inverter side @ Sunsynk.net- Equipment-Gateway select the plant- settings-interval.