Inverter UPS behaviour

Hi, I’m thinking of installing solar plus batteries plus a Sunsynk inverter(s) in the UK. Can I just check a few things re installation/UPS operation please?

  1. UPS capable install requires you to split MCB into Grid and Essentials. A TT Earth wire and Earth-Neutral relay also need to be fitted.

  2. In a powercut the inverter disconnects from the grid (internal operation along with CT clamp) and continues to power Essentials from batteries and/or solar (does solar still work when off-grid?)

  3. If I attach a generator I assume it will only supply the essentials and the batteries?

  4. Is this mode of operation compliant with UK DNO regulations re islanding?


Thanks.

90 weergaven
jacekowski
23 jul 2023
  1. Yes

  2. CT is not used and/or needed in island mode, solar still works.

  3. Yes

  4. Yes

leden

  • Piter Freide
    Piter Freide
  • Will Smith
    Will Smith
  • Rohit Rajput
    Rohit Rajput
  • Orbeat
    Orbeat
  • Andrew Zarudnyi
    Andrew Zarudnyi
Sunsynk Logo.png

Aanmelden

Bedankt voor uw inschrijving!

+44 151 832 4300

+27 101 003589

sales@sunsynk.com

support@sunsynk.com

Documenten

Garantievoorwaarden van de fabrikant

Garantievoorwaarden van de fabrikant - Zuid-Afrika

Uitgebreide garantievoorwaarden van de fabrikant

Milieubeheerbeleid

Beleid tegen fraude, omkoping en corruptie

Beleidslijn voor ethische inkoop

Beleidslijn voor ethische inkoop

RMA Klant Reparatieformulier

RMA Klant Reparatieformulier

Producten

Eénfase hybride omvormer

3,6 kW
3,6 kW Ecco
5,5 kW
5,5 kW Ecco
8,8 kW
8,8 kW Ecco
16 kW

Driefase hybride omvormer

8 kW
10 kW
12 kW
50 kW

Accu's

5,32 kWh
L5.1
L5.3

Hoogspanningsbatterij

Hoogspanningsomvormer

3 Phase 20/25kW

3 Phase 30/50kW

Sunsynk UK Ltd Unit 8, Total Park,

Bennetts Lane, Shell Green, Widnes WA8 0GW

  • Facebook
  • X
  • Youtube
  • LinkedIn
  • Whatsapp

Deel van Sunsynk Group Limited

© 2025 SUNSYNK UK LTD

Geregistreerd in Engeland 8778087

bottom of page