Inverter UPS behaviour
Hi, I’m thinking of installing solar plus batteries plus a Sunsynk inverter(s) in the UK. Can I just check a few things re installation/UPS operation please?
UPS capable install requires you to split MCB into Grid and Essentials. A TT Earth wire and Earth-Neutral relay also need to be fitted.
In a powercut the inverter disconnects from the grid (internal operation along with CT clamp) and continues to power Essentials from batteries and/or solar (does solar still work when off-grid?)
If I attach a generator I assume it will only supply the essentials and the batteries?
Is this mode of operation compliant with UK DNO regulations re islanding?
Thanks.
90 vistas

Yes
CT is not used and/or needed in island mode, solar still works.
Yes
Yes