Answers in same sequence.
1. 3phase 12kw SS inverters
2. 2200ah
3. 39.6kw on 4 of the 8 inverters
4. Max load 75kw
5. No swopped around with nr 8. No difference.
6. Trying to use either Eskomnor generator. Both upstream from inverters. Inverters thus only see grid.
7. All busses and cables calculated to correct sizes.
8. Charge setting set to between 5 to 10 amp per inverter. Doesnt charge effectively. (102 kw generator). Engage, disengage continuously.
9. No all inverters. Doesn stop parallel setup. Still produces power output but doesnt charge.
10 not applicable as generator/eskom connected to changeover upstream from inverters.