(1-Phase house + 3-Phases workshop) on shared batteries

A friend of mine came to my shop with a drawing (see attached below) saying: "Install me this!" I'm not sure if the design is improvable (or even feasable) and I couldn't find any info about that in the forum.





ree

Customer's desired result:

  • House in a remote area, so totally off-grid

  • Two 1phase inverters for the house

  • Water boiler connected to Smart-Load port

  • One 3phases inverter for the workshop (seldom used)

  • Emergency diesel generator connected to GEN port

  • Two batteries (10/15kWh each) shared by the house and the workshop

  • The main idea is "When SOC is low, the workshop can be disconnected and the generator starts" What can I reply to the customer? Can we share the batteries between two different inverter sets (house and workhop)? Thank you Carlo

98 Views

The desing makes sense, but there are other options that give simular fault tolerance and mixed single and 3 phase option at lower cost and with simpler setup:


For 3x single phase Inverters configured in 3 phase confgurations providing both the single phase house load and 3 phase workshop load.

  • All inverters use BMS via the Master inverter

  • There is no technical reason to also have sepearte single phase inverters in addition to the 3 phase configuration as this setup can supply both the single and 3 phase loads.

  • As this is a off grid configuration the generator can be connected to the Grid ports

  • The Smart Load can use the Aux port on the master Inverter.


With this setup the main fault tolernce options are:


One inverter fails:

  • The remaning 2 inverters can configured in single phase parallel configuration

  • The genarator can be connected in single phase to one inverter


Two inverters fail:

  • The remaning 2 inverters can configured in single phase parallell configuration

  • The genarator can be connected in single phase to one inverter


Three inverters fail:

  • The genarator can be connected directly to the consumer loads which would give both single and 3 phase power


The key to designing the solution so it works as intended is good understanding of the loads used by both the house and the workshop.

The battery configuration also need to factor in the maximum power that needs to be drawn from them in the worst case.

With the generator conncted to the Grid ports it can also be configured to provide additional passtrough power when needed.


If the maximum load per phase is for example 5kW per phase for both the workshop and the house loads there are 2 options:

  • 3x 5kW Inverters in 3 phase configuration

  • 6x 3.6kW Inverters in 3 phase configuration and each phase having 2 Inverters in parallel providing 7.2kW per phase.


Although the 6x 3.6kW setup provides better fault tolernce options there is higher inverter internal power use as each inverter consumes ca 60w.