W03 Grid Phase Wrong

Good Day everyone.

I installed 2x12kw 3phase SunSynks yesterday and they both came up with the same fault code. W03 Grid phase wrong. I checked the phase rotation at the point of supply and the rotation is the same through out the original system. Is there a way to check what the phase rotation is on the inverters and if possible change it so it sees the supply as the correct rotation?


TIA

79 Views
Dino Malajika
Mar 09, 2023

Good Day


Please check inverter grid settings. Under phase type 0-120-240 this is anti clock wise. 0-240-120 this is clock wise.