Configuring Battery Capacity
Good day,
I have six lithium batteries (105Ah each) in parallel that I am configuring on a Sunsynk inverter. What battery capacity should I configure here? Is it the sum of the six batteries or I juts put in the 105Ah??
125 Views

If possible connect the battery BMS to the Sunsynk via a Canbus/modbus cable. The BMS will communicate the SoC and capacity. I have 4 x 105Ah (48V) and have configured Battery Capacity = 420Ah Charge Amps = 150A (~7.2kW) Discharge Amps = 150A (~7.2kW)