8.8 Grid Setup Iverter Output Value
Default value for the grid setup is 50hz, single phase with a INV Output V(AC) of 230v. Been advised by installer to set to 240v. Will this be ok? UK based. Thanks
47 Views

Default value for the grid setup is 50hz, single phase with a INV Output V(AC) of 230v. Been advised by installer to set to 240v. Will this be ok? UK based. Thanks
Hi there
I have just been in a 4 month discussion with the DNO and Sunsynk on GRID settings and:
You shouldn't be able to do this AND your installer should not be advising this! You should have G99 selected in the GRID settings adn [with the new firmware] all the connection settings should be grey'd out [G99 requirement] AND settings on page 2 not displayed with text saying 'see table 10.1'.
Do you have this?
Matt
As an aside, the GRID settings on G99 are 230v and many regions like mine are closer to 240v so 240v would be better..... bit with correct settings for G99 compliance you can't change it!