Public·391 members
12kw 3phase - Auxiliary limit
Hi Guys.
I have a question, what is the maximum load you can run on the Aux port on the 12kw 3phase inverter?
and can you run the load on only one phase?
On the picture you can see the load on the aux port is just over 7.2kw (non-essential load) Grid is on and battery is full. ( pv is low) ,problem is that the inverter shuts down after a min or so. for this test the essential loads were mostly turned off because of the inverter switching off.
If I keep the non-essential loads below 6kw then it runs fine...
So, on the UPS side the inverter is capable of running 100% imbalanced loads. But on the Aux side it looks like you are restricted to 6kw Max. Anyone who can confirm this or had a similar issue?
Keith Gough
Keith Gough
Sep 22, 2022
Off grid max 50% unbalanced On grid max 100%