top of page

Technical Support

Public·324 members

Battery not showing SOC on main screen in Battery % mode

Hi,


I have installed 4 sunsynk 5 and 8 kw inverters where I connected lithium batteries and needed to manually setup battery parameters because it's BMS is not communicating with the inverters.


When I set the battery mode to AGM % it does not give me a battery SOC from the main screen. (The other Inverters work fine with the same batteries, accept on these specific inverters)

This gives me a continuous beep and eventually after a minute or so a error F56 apears.


As soon as I change the battery mode to AGM V the SOC shows correctly and Inverter stops beeping and goes to normal opperating. The same error apears again if I attempt to go back to AGM %.


Why would this happen?

Even if the other inverters which the setting is on AGM % settining and work's perfectly is all setup the same as the ones I have on AGM V (which I left on this setting).


Also on the inverters with the battery mode AGM V it discharges the battery all the way to about 0 to 4 % where I specificully set it to discharge to about 50V.

I did for time being set the inverter to not dicharge the battery until I get a fix for this...

The "Time of use" settings is set to discharge to 50V at night time with "Grid Gharge" enabeled.


Please assist??

91 Views
jean1294
jean1294
Jan 10, 2022

Hi Roland

can you please give us the logger numbers and inverter numbers with this problem. Also give us your mail address please.

Members

  • Piter Freide
    Piter Freide
  • Will Smith
    Will Smith
  • Rohit Rajput
    Rohit Rajput
  • Andrew Zarudnyi
    Andrew Zarudnyi
  • Tommy Cooper
    Tommy Cooper
bottom of page