PV voltage 3 phase
I am most likely going for a 3 phase 10K inverter.
According to the datasheet PV input is 550Vd.c (160Vd.c ~ 800Vd.c) and MPPT input is 200Vd.c ~ 650Vd.c.
Would it be ok to have 15 panels in series with a Voc of 40V, which would be 600V?
On some videos it was told not to go beyond 450V, but that only applies to a single phase inverter.
Is that right?
46 Views

Datasheet confirms your reasoning