top of page

Technical Support

Public·322 members

F55 - DC_VoltHigh_Fault

Got this error on an install: F55 - DC_VoltHigh_Fault

8kw unit, single phase, NO battery installed.


Grid voltage was good, grid freq was good - there was actually MORE solar (voltage, current & power) the day before without issue.


So what causes this?


Is it a Battery voltage high? (dont have a battery)

Is it a PV voltage high?


Running 9 panels in 3 strings - Voc 51.4, Vpp 43.2

With 9 panels its 462Voc & 388Vpp



173 Views
Groots
17 ene 2024

At 2:30ish - are you charging the batteries from the grid?

If the temperatures are getting down to 0, have a look at the app anddo a graph to show the actual battery temperature reported by the battery, assuming you have the temperature sensor configured. If he battery temperature is actuall dropping down to 0 then the BMS will stop the inverter from charging the battery. Itcould bethis event that has something to do with your issue.

Members

  • Piter Freide
    Piter Freide
  • Will Smith
    Will Smith
  • Rohit Rajput
    Rohit Rajput
  • Andrew Zarudnyi
    Andrew Zarudnyi
  • Tommy Cooper
    Tommy Cooper
bottom of page