PV Charge Current Limit
This is just a question out of interest
The battery charge current limit is set here and there is a gen charge setting and a grid charge setting.
AFAIK the inverter uses the lower of (this setting and the max charge current reported by the BMS.)

When the PV panels are charging full taps (ie there is enough power being generated to meet the charge limits) , does the PV "current" limit fall under the grid setting above ?
84 Views
PV charge limit is set in the battery setup page. The above page is for grid or gen charge.
As mentioned - the lower of BMS or PV charge limit will apply.