Sunsynk 5kW and generator not working

I'm looking for some assistance in getting my generator working with my Sunsynk 5kW inverter...

I recently decided to buy a generator, mainly for help run the load and recharge the batteries when we have extended and/or morning load shedding. I got a Ryobi RG-7900k, 7kW rated with a peak of 7.9kW.

This morning I had the chance to try out the generator as the power was off, again...

I have the generator wired to the AUX connection on the inverter.

When I started the generator and switched on the circuit breakers the inverter do not use the power. I confirmed the generator power was reaching the the inverter by checking the voltage at the inverter connections using my multimeter.

I do have a contactor for earth-neutral bonding when the grid power is off...

here are what I believe to be the relevant settings





I did notice that while the generator was running the grid frequency showed as the frequency the generators display panel showed as seen in this image.

If I switched off the circuit breakers between the generator and the inverter then the grid frequency remained static at the last reading and then fluctuated a little again when switching the circuit breakers on again...



Please could someone let me know what I've missed and need to change or what else to look for...

123 Views
Rhys
Dec 12, 2022

Thanks Keith, I had found the video, which did help and showed me a few things to set. The only thing I don't recall from the video was about earth/neutral bonding on the generator side of the connection which is the only thing I had not done. Once I did that all seemed to work just fine.