Hi what figures should I put in when it ask for ah rates when setting up batteries
Thanks Warwick
In the Battery Setup page, you just need to set your total Capacity (Each Pylon has 74Ah - so e.g. 5 Pylons would equate to 370)
As long as your inverter is connected to the Pylon BMS, it will get all other info directly from there
(Charge and discharge rate for each Pylon is 37A, but it will take this figure from the BMS)