Master Inverter using 1.4kw from the grid when PV available

Have 2 x 8Kw inverters, the Master is now consuming 1.4Kw from the Grid even though there is PV and battery available the slave is only consuming 40 watts. I have confirmed this using tounge ammeter (6.3 amps) around inverter cable and the utility meter.

Why is it consuming such a large amount?


David


2 x 8K SG01LP1-EU COMM:e424-MCU:5374

36 x JA 540w panels

9 on each MPPT on each inverter

9 x PylonTech 4.8Kw Batteries



54 Views

Is your system setting for the very time slot not perhaps set to charge battery from the grid to a certain %, whilst the battery at that stage was below the set %