DynessF10 on BMS control & "Load priority" on Sunynk active, PV production falls away totally when bat charge reaches 100%.

When Dyness F10 is under BMS control & "Load priority" on Sunynk 8kW is active, PV production falls away totally when the battery charge reaches 100%. When unchecking "Load Priority" the PV production returns.

How do we stop the PV production from disappearing when the Dyness F10 Powerbox is 100% charged, while at the same time keeping "load Priority" checked?


PS, when the Dyness is under manual battery settings, this scenario does not occur!

70 Views
Blake
Apr 24

The firmware update seemed to sort it all out. No problems since then.🎈