Slave not reading settings from master
Hi.
I had 1x 5kv sunsynk inverter and 1 5kv sunsynk battery.
I added another 5kv sunsynk inverter and another 2 batteries.
The problem I am having is if I change the settings on the master it does not change on the slave.
The inverters are in parallel.
Any idea what could be the issue..?
Thanks in advance.
Regards
38 Views

Check coms cable between inverters and inverter addresses. My system is set as master address 1, slave address 2