Shut Down, Low Batt, Restart - Battery Setup
I'm trying to understand what would be good % for the battery setup screen, specifically the shut down screen on the Sunsynk 16K inverter. I've looked around on forums/youtube and they simply say its up to you, which doesn't help if you don't really know what would be a good starting point. We are using 10.25kw GSL batteries, with thw 16kw Sunsynk Inverter and I would like to understand what to set the Shut down, Low Batt and Restart to? If anyone is able to help on how I go about determining these values.
81 Views

I have the 8.8kW Sunsynk Ecco with 30kWh of Fogstar batteries. My settings are "Low Batt" 18%, "Shutdown" 15%, "Restart" 20%. This means I get a warning at 18%, the batteries shut down at 15% and restart when they have been recharged to 20%.