top of page

Technical Support

Public·330 members

Sunsynk settings not locking

Hi everyone. I have a site with 5x 12kw sunsynk inverters with 8x 14.3kwh solarmd batteries, all in parallel. The issue I am facing is the master is not retaining set parameters e.g. it keeps reverting back to AGM V on battery type from the set Lithium option. Time of Use settings hold for less than 2 min and revert back to default settings. Can anyone kindly assist?

59 Views
jasper mubango
jasper mubango
Jan 15, 2024

Managed to get it right by bringing in the slaves one at a time until all synced well. Very strange...

Members

  • Piter Freide
    Piter Freide
  • Will Smith
    Will Smith
  • Rohit Rajput
    Rohit Rajput
  • Andrew Zarudnyi
    Andrew Zarudnyi
  • Tommy Cooper
    Tommy Cooper
bottom of page