Sunsynk settings not locking

Hi everyone. I have a site with 5x 12kw sunsynk inverters with 8x 14.3kwh solarmd batteries, all in parallel. The issue I am facing is the master is not retaining set parameters e.g. it keeps reverting back to AGM V on battery type from the set Lithium option. Time of Use settings hold for less than 2 min and revert back to default settings. Can anyone kindly assist?

59 Views
jasper mubango
jasper mubango
15 jan 2024

Managed to get it right by bringing in the slaves one at a time until all synced well. Very strange...