With an external CT using Modbus comms, there is a problem and the link is broken (for what ever reason), the Inverter throws a W04 fault and this will not clear without a full shutdown and restart of the inverter. A restart always fixes the issue.

This is a pain and is quite limiting.

I would suggest that there is a firmware upgrade that has some form of watchdog and then a reinitialisation of Modbus comms when a W04 fault and External CT is in use. This would then prevent a fall restart.


For info, I have tried with no positive result

1. To restart the slave of the Modbus

2. To leave for a period of time

3. Improve the RS485 link - does help

4. Change the settings from Internal to External CT


It seems to be that the solution is probably a firmware update.


101 Views
Groots
Oct 03, 2024

I am not familiar with the ESMB1 Modbus Wifi Bridge, but looking up the specs they should do the job.

I had the same issue with a 3 phase version of the Eastron meter. I had to get Sunsynk to send me an official version (that they provide) and this resolved my W04 warnings.

Which SDM120 meter do you have?

What is the CT ratio ?

My personal system use a SDM120CT-MV with a 120A/40mA CT and is also connected using a Solax Wireless bridge and it works well. The only time I get a W04 warning is when I power off the wireless bridge.