2x 8kw in parallel and 9kw pv and 4 battery 20kw

Right we are starting to fit parallel 8kw inverters what i like to know as i cant find anywere have i got split the pv half in one inverter . and half in other inverter or can it all go on the master .sunsynk 5.12 batterys can they all connect together and then i split the output two the two inverters or should i do 2 batterys on one inverter and 2 on other sorry if it sounds silly but just want to make sure thanks patrick

80 Views
Groots
Jul 15, 2024

If the inverters are in parallel, the batteries must all be in parallel. Create a common bus and connect the 2 inverters to the bus.

The batteries will have one master and 3 slaves.

The inverter will have a Master and Slave.

The master battery comms connects to the master inverter using CAN bus.

You say yo have 9kW of PV, but not what size panels. Lets assume you have 20*450W panels. To ensure that you maintain a good Voc I would suggest you split this in to 2*10 panels strings and use the master inverter, however for redundancy you could put one 10 panel string on each inverter.