Lifelynk X export limiting
Hi can the lifelynk X be export limited ? not to exceed 3.6kw when used with another inverter which is on the FIT scheme.
does it use the CT clamp to read the output . if maximum output to grid is set to 3600w on the lifelynk and my FIT inverter is exporting 2600w will the lifelynk limit it self to 1000w as it is reading the CT clamp on the main grid cable or will it export at 3600w?
63 Views

My understanding is that the are set to zero export by default - as long as you put the CT coil in the correct location. So that the app and screen report the correct imported power the inverter will need to be connect in front of the current FIT inverter - between the FIT inverter and the the live cable on the mains power meter.
This may not be possible, but in either case, the CT is between the SS invert and the live cable and the mains Power meter