Hi I am in the process of installing a rack mount Sunsynk 7.6kw inverter. At this stage I wont have any PV panels as I live in a complex. Since I have gas geysers and gas stove I am considering powering the whole db board from the load output of the inverter as UPS. I understand that the load output is limited to the inverter size when in island mode. My question is when there is no load shedding and drawing from the grid, is this output active and is it still limited to the inverter size? Thank you!

138 Views
jacekowski
Feb 24, 2023

That's not what the datasheet says unless we are looking at a different inverter. but the one i've found for rack mount 7.2kW says 50A in passthrough mode, so closer to 11.5kW.


There is still an issue of changeover from passthrough operation when grid is available and load being supplied from inverter only, where if there is more load than inverter can deliver is island configuration it will shut down.