Power limit when using AC coupled inverter on Aux load?
If I have a 5kw Sunsynk with a 4KW PV array. What is the maximum power auxiliary port can handle from an AC coupled inverter?
218 Views

If I have a 5kw Sunsynk with a 4KW PV array. What is the maximum power auxiliary port can handle from an AC coupled inverter?
Hi @africaengineeringideas it seems the sum of the UPS & Aux circuits are only limited by the "Max Bypass" current of 90A (+-20kW) while connected to Grid, and again the sum of both is limited to the 8kW when no grid available. Hope that helps.