Inverters pulling eskom load
Good day please i need some help
I have been battling with 2 x 12kw 3phase units in parralel for a week and cant get assistance.
Batteries is let say above allowable soc set in timers so let say soc is 99%, in timer set at 60%
More than sufficient solar available
Inverters show no grid is consumed except the normal 0.2kw "trickle feed"
But if messured below the grid input each phase is pulling between 1 to 3 amp
If "Limit to loads only" is *selected* (meaning only essentials)
Loads for example will 2.5kw each inverter
Inverter showing no extra grid consumption
But if measured below grid input a excessive reading found.
If "limit to loads only" is *not selected* (allowing non essential items to be supplied)
Loads drop to example 400w per inverter
Inverter showing no extra grid consumption
But if measured below grid input a reading of double above is found example 7-8kw.
If grid is switched off i want to say true readings are found on loads.
The SA whatsapp group have updated software but does not solve the issue.
These 2 units are pulling 70-110 units per day from grid for no reason.
What can the cause be?
I have factory reset, software done, swoped master and slave.......

Are the inverters on the same firmware versions?