Inverter charge settings

I believe this is a very simple question, but the reason I am puzzled is I assume the installers knew what they were doing...


I have a Sunsynk 10K SG04LP3 (3 phase, 10kW) hybrid inverter, sitting between 10kW of PV panels and about 30kWh of batteries. The batteries are 6 Pylontech US5000 (4.8kWh, 100Ah). They have a maximum stable charge current of 80A. They have been installed in parallel, in 2 blocks of 3 - see photo. I understand the current limit for the cables is 100A, so the total cable limit is 200A.


The installers have set a max charging current of 80A at the inverter. As a result, the charging power is 'throttled' at 4kW, and when the PV panels are outputting more than that, the excess goes back to the grid for buttons.

As I understand it, the inverter 'sees' the batteries as a single 600Ah 48v block. As such, the maximum charge for the block should be 6X80A = 240A, but limited to 200A by the cables. So it seems the present 80A limit is wildly wrong. Am I missings something, or have the installers just phoned this in?



82 Views
thebaps1
thebaps1
Jun 10, 2023

Very good point, the installation manual even shows two sets of cables being needed per bank for 200A.