Display Bug on System Flow Chart: UPS watts shows incorrectly as total of essential load and aux/smart load.
Hi, I think there's a display bug on System Flow Chart. please attached photo.
In this case there was a tiny load on essentials/UPS (+-50 Watts just a few lights) and a +-1.75kw load on Aux\Smart output. The inverter is correctly supplying 1.8kw+.
The watts displayed for UPS (essential load output) is the same than the total watts being outputted by the inverter. If there was no aux\smart load it would have been fine. But, not if there is Aux\Smart load then the UPS load is incorrectly showing the combination of essential load and aux/smart load.
This inverter is 8kw and running Firmware: M 6.0.1.4 / S 2.4.1.7 / C E.4.2.4

51 Views

Hi Nicholas. Yes non-essentials is running of aux port and feeding off battery if PV is not enough (in line with the system mode power level and SOCs ofcoures). In the picture in post 1 the power came from a combination of PV and battery and zero from grid.
I'm willing to update firmware to see if its perhaps fixed there already.
My question, or rather concern, around firmware update is whether its still true that there should be no load output from inverter and no PV input to inverter when update is happening. As the update are done remotely from a request we don't really know when it will occur so I can't make sure that there's no load or PV at point of update.