Exporting excess solar
I feel like i'm going round in circles with export. There appears only to be 4 buttons to choose from
Zero Export
Solar Export
Limit to load only
Priority load
but so much conflicting information online and on the Sunsynk youtube channel. They have changed the screens on the inverter so the the tick box 'sol exp bat full' has gone. Has that been replaced by simply 'Solar export'?
Keith had 'zero export' and 'sol exp bat full' ticked at same time!!!
can anyone usining solar export successfully share a pic of the settings they have on the inverter please
NOTE the image below is from the old inverter screen.
Thanks in advance
<image removed as was causing confusion>
apologies
305 Views

This is how you'd want it set if you want to fill you battery up at night on E7 then discharge it to your house during the day and any excess solar (once battery if full and your load in the house is satisfied) is exported to the grid.
The SOC on the timer page is really a min charge you want your battery to be during that time. If you have the Grid charge for that time ticked, it will pull from the grid to achieve that. During the day you want it low so you house can pull from the battery and use that instead of the grid.