Seplos advice needed

Hi Sunsynk setup working well....however the battery is giving me some issues have a 16S Seplos BMS 200a my battery has a theroretical capacity of around 15kw using 302amp cells. Communication is good no issues there. However...I have been running out of power over night...the battery gets down to around 35% state of charge and then plummets to 10% then grid charging kicks in.............. I then checked the Sunsynk battery charge and discharge history............basically it is charging up around 5kw and discharging 5kw....... ie around 100amps.... So I went into the Seplos BMS and found the following....

ree

So - it appears to me that I have inadvertanly set SOC to 100 (thinking it was percent) ... underneath it says Ah ...... so should this parameter be set to 302???? can anyone advise...

64 Views
Hermit Dave
Hermit Dave
Jul 07, 2023

I have 2x Seplos with 280Ah batteries and one of them had an issue where it wouldn't let me change from 200Ah to 280Ah. I had to resort to creating a rs485 to usb cable (picked up £9 adapter from Amazon) and using their windows software