Clean Voltage ouput
Hi
My supplier are not able to supply me with clean voltage. Voltage vary from 190-225V depending on the load in town. I dod set my low votage to 210 to prevent Damage to my equipment. But I dont get enouth clean voltge from grit to charge my system diring night time. The inverter keep connetcing and disconecting and electrician are not skilled to ballance phases correctly or check for hot connections to solve problem.
Sunsynk dont have the option to supply stable voltage and only charge battery with the bad voltage? I even tried the Gen input by it also go to bypass. I would have thought that an advansed unit like Sunsynk would use the gen input to only charge the battery and not pas thougt the bad generation of most generators.
Any advice exept installing an extra inverter for only battery charging?

First of all there is no inverter that is a power conditioner. The inverter will follow the grid voltage and frequency with the limits set.
Looking in the manual, the defaults are:
These settings provide a wide tolerance. If you are experancing voltages outside these limits you definitely need to investigate other options and this will start affecting the functioning of connected loads.
WRT to you comment about the GEN port - when the inverter is connected to the grid, the GEN port which is on the same common AC power bus has to follow the Grid voltage/frequency.